M msi99 Member Location Texas Occupation Solar Jul 31, 2024 #1 To determine the needed clearance from a Weatherhead to a Weatherhead run between 2 structures on the DC side of a solar installation, we would still have to refer to 225.18, right? 255.18 (3) to be specific.
To determine the needed clearance from a Weatherhead to a Weatherhead run between 2 structures on the DC side of a solar installation, we would still have to refer to 225.18, right? 255.18 (3) to be specific.
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Jul 31, 2024 #2 I agree. (Assuming the voltage is between 300 and 1000 volts.)