For decades for a 1st cut number have simply used 300 NH per foot or 1 uH per meter. As good as anything for mast cases.
If critical applications, either mock it up and measure or use one of the electromagnetic FEA analysis programs
For aerospace use even the fancy/pricey full FEA programs relay on correct inputs, so nearly always do a mockup and measure, have never trusted models or calculations for critical/complex systems.
Just because you can calculate it does not mean your inputs are correct, as per the 1960 computer sayings, 'garbage in, garbage out".
the point is it is inconsequential for a 125 vdc ckt of conductors in a conduit
there is a reason the nec gives tables
but a typical nec conductor x/r is ~ 0.05 inductive, very minute ckt response influence
Example #10 Cu
Xl 0.05 or L 0.132 mH/1000'
R 1.2
X/R = 0.044
tc = 0.132 x 10e-3 / 1.2 = 0.11 x 10e-3
observe at 0.001 sec (0.06 cycle 60 Hz based)
i = max x e^- (0.001 x 0.00011) = max x 1.0000
current rises to max 100% in 0.06 cycles
does not matter unless dealing with very hi freq signals
and never worth measuring in this application
in fact pointless to even use the table values
does not matter either way
that is why it is usually ignored in power level calcs