DC source circuit conductors inside wall?

Status
Not open for further replies.

Zee

Senior Member
Location
CA
Can I run DC source circuit conductors, in EMT, inside wall?
Does it change things if it's optimizers?
How about rapid shut down?
DC Disco on roof?
 
Can I run DC source circuit conductors, in EMT, inside wall?
Yes.

Does it change things if it's optimizers?
Maybe it changes the nitty gritty of some code requirements (technically that's not a source circuit anymore), but you can still do it.

How about rapid shut down?
Doesn't change anything.

DC Disco on roof?
Doesn't change anything.
 
thx

To be clear: no provisions must be made to de-energize the conductors if inside wall?
 
thx

To be clear: no provisions must be made to de-energize the conductors if inside wall?
The NEC does not require it of PV source circuits but your AHJ might. But 690.15(C) says that if you combine strings on a roof you must have a disco up there.
 