The takeaway here is that you have less flexibility for diversity among the strings, when one of your strings is between the standard upper limit of 6kW and the fine print upper limit of 6.5kW. The inverter has to increase the voltage above 400V, in order for a string to operate at 6.5 kW. All strings that are paralleled need to operate at the same DC voltage to meet Kirchhoff's voltage loop law. The higher the voltage, the harder it is for your smaller strings in the same parallel group to catch up with the larger strings, to achieve the same voltage.