I have a big problem on my hands that I can't seem to find a definite solution too, atleast that others will accept. There is much debate as to what the proper equation for voltage drop is when dealing with DC power. I have consulted various references (including this site) and cannot find a difference between AC single phase and DC voltage drop calculation. Heres the equations that I have been using:
1-Phase
VD = [2 x K x (length) x (load)] / CM
3-Phase
VD = [1.73 x K (length) x (load)] / CM
The people I am dealing with insist the equation is wrong for DC and cannot be applied. Can anyone give me any insight. Here's some sample data that I have for calcs if anyone is interested.
K = 11.1
L = 60 ft
I = 1200 A
CM = 211600cm (4/0)
VD = [2 x 11.1 x 60 x 1200] / 211600 = 7.55 volts
This all leads to my next question. Does the Code assume that the input voltage of the system is the same as the output voltage of the system even under load? Is there a voltage drop percentage in the code other than for Branch Circuits (2%) and Feeders (3%)?
As always, thanks in advance.
John
[ February 17, 2004, 06:19 PM: Message edited by: jsinclair ]
1-Phase
VD = [2 x K x (length) x (load)] / CM
3-Phase
VD = [1.73 x K (length) x (load)] / CM
The people I am dealing with insist the equation is wrong for DC and cannot be applied. Can anyone give me any insight. Here's some sample data that I have for calcs if anyone is interested.
K = 11.1
L = 60 ft
I = 1200 A
CM = 211600cm (4/0)
VD = [2 x 11.1 x 60 x 1200] / 211600 = 7.55 volts
This all leads to my next question. Does the Code assume that the input voltage of the system is the same as the output voltage of the system even under load? Is there a voltage drop percentage in the code other than for Branch Circuits (2%) and Feeders (3%)?
As always, thanks in advance.
John