The NEC is not a standard period. It is a set of minimum safety requirements. Further there is NO requirement in the NEC for voltage drop for either AC or DC.anbm said:What's standard for DC voltage drop - branch circuiting? Is it still 3% as AC per NEC? Thanks!
Again there is no requirement, it is a design issue, All the NEC stipulates the minimum wire size based on the over current protection device size.anbm said:Derekbc,
So what is the minimum safety requirements for 12VDC - VD if you know?
Well the NEC table 310.16 requires a minimum 12 AWG to be perfectly safe. However your voltage drop using 12 AWG with 20-amps at a 1-way distance of 130 volts is roughly 8.8 volts. Not acceptable IMO on a 12 volt circuit.anbm said:if my load is 20A, 130ft of feeder), then I can calculate the wire size based on this minimum requirement?
If the DC is produced from AC 120V using a trensformer rectifier unit or some other converter, couldn't you put the converter closer to the load?anbm said:Derekbc,
So what is the minimum safety requirements for 12VDC - VD if you know?
(if my load is 20A, 130ft of feeder), then I can calculate the wire size based on this minimum requirement?
Off on a complete tangent.....dereckbc said:I work in the Telecom industry and we have very strict DC voltage drop requirements for 48, 24, and 12 VDC systems.
Certainly and that is exactly what is done by using smaller capacity plants called Distributive Power. Catch is two fold it requires VRLA batteries which needs replaced every 5 to 7 years as opposed to 20 to 50 years with a flooded battery, and much higher initial upfront cost.Besoeker said:If the DC is produced from AC 120V using a trensformer rectifier unit or some other converter, couldn't you put the converter closer to the load?
Yes they are still stingent. For example Marconi Vortex Phosphometric Noise is less than 1 mV.Besoeker said:From what I recall, the ripple requirements were very stringent - psophometrically weighted with around 2mV in the audible range.
In your experience, is this still a typical Telecoms requirement?
Interesting link, thanks.dereckbc said:Yes they are still stingent. For example Marconi Vortex Phosphometric Noise is less than 1 mV.
I was replying to anbm's post and I don't know what his application is so I wouldn't know whether his/her application requires batteries.dereckbc said:Certainly and that is exactly what is done by using smaller capacity plants called Distributive Power. Catch is two fold it requires VRLA batteries which needs replaced every 5 to 7 years as opposed to 20 to 50 years with a flooded battery, and much higher initial upfront cost.
dereckbc said:Yes they are still stingent. For example Marconi Vortex Phosphometric Noise is less than 1 mV.
With enough L and C it can be done.physis said:Wow, 1 mV, that's pretty demanding. I'm sort of surprised it can even be done practically.
Yes th eVortex line is Switch Mode. These are farly small rectifier units installed in a equipment shelf with self contained distribution. You see a lot of htese in vey small sites like Cell Towers.Besoeker said:Interesting link, thanks.
It sounds like it could be a switch-mode front end. At a little over 3kW per PCU, it's a practical option.
Actually it is a common specification from all Telco grade DC plants. Once you put a sting of batteires across it even drops significantly lower by the filtering charaterisitcsphysis said:Wow, 1 mV, that's pretty demanding. I'm sort of surprised it can even be done practically.
I have used Yuausa, Excide, C&D plus many others. After years of load test we found after 5 to 7 years their rated capacity drops below 75%. So instead of spending the money on load test, we just replace them every 5 to 7 years.Besoeker said:On the VLRA topic, we generally use Yuasa ENL series which have a stated life of 15 years. .
That kinda illustrates my point - you'd need 40 units in parrallel to get 8kA.dereckbc said:Yes th eVortex line is Switch Mode. These are farly small rectifier units installed in a equipment shelf with self contained distribution. You see a lot of htese in vey small sites like Cell Towers.
I use a lot of Marconi rectifiers and they make a 200-amp modular unit I and use them in a lor of 4000, 6000, and 8000 amp DC plants at 48 volts.
I agree with all of that.dereckbc said:Well to be fully honest for the large DC plants say 6000 amps and higher we use 3-phase transformer SCR rectifiers rated at 800-amps per cabinet made by Marconni. They take up more space, weigh a ton, but practically indestructable and last forever. Switch mode rectifiers have high failure rates so this is why they are small in comparison and if you loose one, the others in parallel are more than capable of picking up the slack.