Kurt Vilary
Member
- Location
- South Jersey
310.15(B)(3)(a)(4)
Adjustment factors shall not apply to Type AC cable or to
Type MC cable under the following conditions:
a. The cables do not have an overall outer jacket.
b. Each cable has not more than three current-carrying
conductors.
c. The conductors are 12 AWG copper.
d. Not more than 20 current-carrying conductors are
installed without maintaining spacing, are stacked, or
are supported on “bridle rings.”
Thanks for your help Lucky. That is what I was looking for. But, as I continued reading...
310.15(B)(5)(a) Neutral Conductor
A neutral conductor that carries only the unbalanced
current from other conductors of the same circuit shall not be
required to be counted when applying the provisions of 310.15(B)(3)(a).
I interpret that to mean we are compliant using 12/4 or 10/4 as a home run for 2 separate 120v circuits (2 hots+2 neutrals) with out derating as per 310.15(B)(3).
Correct???
KV