- Location
- Massachusetts
IMO derating should be considered for the branch circuiting in situation like this:
I was doing some IR scans today that prove that to be the case.
IMO derating should be considered for the branch circuiting in situation like this:
But how do you determine the ampacity with the physics (enclosure v. raceway) not the same.The physics of bundling remains the same.
But how do you determine the ampacity with the physics (enclosure v. raceway) not the same.
Is bundle on ladder-type cable tray different than bundles in wireway
In a sense yes, if you want to put it that way.So you are saying there are no NEC ampacities for inside enclosures?
Ok, then where does the section I quoted that talks about single conductors being bundled for 24" or more and not installed in a raceway apply?In a sense yes, if you want to put it that way.
What I am saying is ampacity is determined outside the box (pun intended :thumbsup and that's all that is required by the NEC.
Perhaps areas of intent... perhaps not. We may be able to go back through the proposal(s)—nka public inputs—to glean more of the intent, but a well written section requires no such action.Ok, then where does the section I quoted that talks about single conductors being bundled for 24" or more and not installed in a raceway apply?
In my opinion it applies to the control panel in the pictures that are in this thread and also within vertical and horizontal wireways in a MCC.
How can we apply that section if we cannot assign an ampacity? How do we know this short portion of the circuit has a higher or lower ampacity?That being said, the exception in 310.15(A)(2) would often apply to those applications.
I was thinking the same thing ....
Derating will seem to follow more a long as in a Pan or a Traugh ....Wire way ... # of conductors across a certain area ...
There is NO Pipe restriction for heat to gather .,,,
Cotinious or not shall matter .
Don
In a sense yes, if you want to put it that way.
What I am saying is ampacity is determined outside the box (pun intended :thumbsup and that's all that is required by the NEC.
Perhaps a colloquialism that I'm not familiar with... so I'll ask. What does that mean?I think this thread has jumped the shark.
Rather than trying to explain it I will just refer you to a vetted Wikipedia article.Perhaps a colloquialism that I'm not familiar with... so I'll ask. What does that mean?
Perhaps a colloquialism that I'm not familiar with... so I'll ask. What does that mean?
It's far from the first time I've mentioned it. Apparently it wasn't so far fetched the other times. :lol:It means I think that idea you proposed is so out there I have no way to respond to it.
It means I think that idea you proposed is so out there I have no way to respond to it.
FWIW, I don't see Bob's meaning from that write up.Rather than trying to explain it I will just refer you to a vetted Wikipedia article.