O.K. that number looks like ITE EQ8695 ,. in which case that is most likley a used breaker,.. I might be missing something ,...but I fail to see the phase to phase fault:-?
The fault is in the wiring. The bus on the panel is set up as A B A B A B. When they split the stranding on the wires, they landed each half of the same wire on a different phase.
The only way to be sure is for Kevin to post the part number of that breaker so it can be properly identified. Because like it or not, it could be made as either AABB or ABAB and we won't know for sure until we get the scoop on the actual breaker involved.
Regardless, the splitting of the strands (and a few were cut off if you look really close) is hack and reason enough to red-sticker it.
No, this type of 4-pole breaker is four individual bodies. There's no swapping-around of the conductive pathway.The only way to be sure is for Kevin to post the part number of that breaker so it can be properly identified. Because like it or not, it could be made as either AABB or ABAB and we won't know for sure until we get the scoop on the actual breaker involved.
Do you mean like this?,,
![]()
No, this type of 4-pole breaker is four individual bodies. There's no swapping-around of the conductive pathway.
The factory-installed main shows that, and that the second 4-pole installer didn't know what he was doing.
The only way to be sure is for Kevin to post the part number of that breaker so it can be properly identified. ....
Correctamundo!Well in that case ,... there is a phase to phase fault :smile:
I'd bet my sox it's an ITE EQ9685