WA_Sparky
Electrical Engineer
- Location
- Vancouver, WA, Clark
- Occupation
- Electrical Engineer
I'm working on an apartment complex that is getting a little uncomfortably-high in the amperage. Anyone want to shed some light on this topic?
This multi-building, 75 unit apartment complex, 208 single phase service is showing roughly 3400A demand after nec factors and all have been applied. Eaton has gear that can handle up to 5000A for group metering but im hesitant to continue with design on one single service feed due to potential SCCR problems down the road.. I'm expecting my MDP and disconnect to be rated for 4000A... Is it pretty common to work with amperages these high in 208-1Ø? Any other possible concerns or problems i should be aware of down the road?
This multi-building, 75 unit apartment complex, 208 single phase service is showing roughly 3400A demand after nec factors and all have been applied. Eaton has gear that can handle up to 5000A for group metering but im hesitant to continue with design on one single service feed due to potential SCCR problems down the road.. I'm expecting my MDP and disconnect to be rated for 4000A... Is it pretty common to work with amperages these high in 208-1Ø? Any other possible concerns or problems i should be aware of down the road?