electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
The only way I could see making a system work would be to choose series rated breakers so the 20A/1p are rated for 65K with their upstream device.
And that can easily done, but the upstream device can't be very large. I stated earlier typically larger than 400 amp frame, but I remember now, with Siemens anyway, it's even lower than that You won't be able to go from 65k down to 10k with anything over 250 amp for the upstream Device. You can go up to 2000 amp for the upstream if you use the "H" series (22k) breakers. Again this is Siemens, I didn't check other brands for a better deal, but assuming they are similar.