Well, I know this is going on AGAIN!! I think I 'upset' my fellow electrician. But he claims it would be 'grandfathered' in, and I told him no it would not according to the manufacturers instructions.
He replaced a baseboard heater under a receptacle (its about 10" above the heater, but the cord can't stay away more than 6") and he says since he's just replacing the 'existing' baseboard heater that was already under the receptacle, he's fine.
I say no, because the instructions CLEARLY say
He's mad at me now over this issue. I know, Im being technical again, but hey as a famous man said, 'It is Written'.
What do you think??
He replaced a baseboard heater under a receptacle (its about 10" above the heater, but the cord can't stay away more than 6") and he says since he's just replacing the 'existing' baseboard heater that was already under the receptacle, he's fine.
I say no, because the instructions CLEARLY say
This is where NEC 110 2008 would come into play. I say it's a new heater and you have to follow their instructions, and this cannot be grandfathered.instructions said:do not install under receptacle outlets, and keep electric cords etc.. at least 6" away.
He's mad at me now over this issue. I know, Im being technical again, but hey as a famous man said, 'It is Written'.
What do you think??