I am amazed at the fine detail I pick up here with you folks. Thank you all so much. This is a big improvement on my initial solution.
Optimal solution so far is:
Optimal Solution to Date.........
3 sets of #12 derate to 21A (with no other derating), should sufficient for a 21.10 MCA. 220.5 permits us to round fractional ampere values to the nearest whole number. However, there may be some question whether that stipulation carries to other articles, or more specifically where no calculation is performed, such as in this case the MCA being a rating, not a calculation. Opinions?
I am amazed at the fine detail I pick up here with you folks. Thank you all so much. This is a big improvement on my initial solution.
Optimal solution so far is:
To install 5 Outside Units about 50 ft from the 480/277 panel:
[*=2]Run 2 3/4" EMT's
[*=2]Pull 3 sets (A,B,C) of #12's in first (9 wires)
[*=2]Pull 2 sets (A,B,C) of #12's in second (6 wires)
[*=2]Use 3 pole 25 amp common trip circuit breakers for each set (5 x 3-pole breakers)
Note 1: No neutrals are to be run
Note 2: Because it is a/c compressor equipment the small conductor rule is ignored so #12 is rated for 30A
Note 3: EMT conduit used as ground
Any corrections or comments????Note 3: EMT conduit used as ground