If your jurisdiction has adopted the ICCEC or Appendix 'K' of the 2012 IBC (Administrative Provisions for the NEC) They specifically state that single- and mutiple-station smoke alarms installed within dwelling units shall NOT be the only connected load on a branch circuit. Such alarms shall be supplied by branch circuits having lighting loads consisting of lighting outlets in habitable spaces.
But it does not state any requirement for "other than dwelling units". :ashamed1:
K111.6 Smoke alarm circuits. Interesting
Nec commentary
Single and multiple-station smoke alarms, such as those commonly installed in dwelling units, are supplied through 120-volt branch circuits rather than through a non?power-limited or power-limited fire alarm signaling circuit that is powered and controlled by a fire alarm control panel. Branch circuits supplying power to single- and multiple-station smoke alarms are not subject to the requirements of Article 760.
IBC does not cover"
Exception: Detached one- and two-family
dwellings and multiple single-family
dwellings (townhouses) not more than three
stories above
grade plane in height with a separate
means of egress and their accessory structures shall comply with the
International Residential Code.