I am led to believe that the NEC requires dedicated circuits to serve major kitchen appliances (i.e. oven/range combination).

I have a second kitchen in my home that gets seldom use and I wish to use the 240v line serving the stove to power another appliance requiring 204v service (i.e. clothes dryer), would I be compliant if I had a switch installed that would allow me to switch the voltage between the stove and another appliance such that when one were in use the other would be disconnected from the power supply and vice versa?
 
Re: Dedicated Circuits for Kitchen Appliances

I am putting a temporary hold on this thread. I am taking this action because the thread appears to me to be an attempt by a Do It Yourself person to obtain "how-to" information. The Forum?s rules do not permitted us to provide ?how-to? assistance to a person who is not employed in this industry.

I invite the Original Poster to send me a Private Message, to explain the circumstances, and to let me know if I have misjudged the circumstances. If you do not know how to sent a PM, then check out the FAQ thread at the top of the list of topics.
 
Re: Dedicated Circuits for Kitchen Appliances

This thread had been temporarily moved to an area accessible only to the Moderators. This action was taken because it appeared to be an attempt by a Do It Yourself person to obtain "how-to" information.

In an exchange of Private Messages, the Original Poster has provided assurances that this is not the case. In this case, the OP stated that he is merely looking for options to discuss with the electrician that he will hire to complete the project. Therefore, the thread is being returned to the active area. I offer an apology to the OP for the inconvenience and the delay.
 
Re: Dedicated Circuits for Kitchen Appliances

There is no reason for a switch.

However the stove is a 40 or 50 amp circuit and the dryer requires a 30 amp circuit. This will be a problem.

You can not feed the 30 amp dryer with a 40 or 50 amp circuit.

Best bet is to run another circuit from the panel.
 
Re: Dedicated Circuits for Kitchen Appliances

Originally posted by KDYMANIAC: I am led to believe that the NEC requires dedicated circuits to serve major kitchen appliances (i.e. oven/range combination).
You were misled. Or perhaps you misunderstood what you were told. There is no such rule. However, there are rules about having the rating of the circuit (defined as the rating of the breaker) not exceed the ampacity of the conductors or the rating of any switches or receptacles along the path. There are also rules that limit the amount of load that you can draw from a single branch circuit.

I have to agree with Bob (Iwire); the best solution is to run a separate circuit. I don't think any other plan would save you much (if any) money, and this solution keeps it simple (i.e., no confusion over what circuit feeds what load at what time).
 
Re: Dedicated Circuits for Kitchen Appliances

There is another option that could save running a new circuit, but may not be cheaper overall: Run the existing range feed to a 4-space panel, and place a 40a 2-pole for the range and a 30a 2-pole for the dryer.

The original breaker in the panel would protect the feeder, and the dryer's feed can be 10 gauge as usual. One possible issue might be that the new feeds could be called "new" and require insulated neutrals.

Just food for thought.
 