Grouch
Senior Member
- Location
- New York, NY
Dedicated electrical space is required, per 110.26(E), above switchboards, switchgear, panelboards, and motor control centers. I believe the answer is no, but does this apply to meter centers?
Each meter has a circuit breaker adjacent to it.If it's only meters then no.
So then it's service equipment so yes it's required.Each meter has a circuit breaker adjacent to it.
No no, this is not service equipment... sorry if I caused confusion. The service equipment, further upstream, feeds the downstream meter center.So then it's service equipment so yes it's required.
Do the innards include "buses and automatic overcurrent devices," and are the innards "designed to be placed in a cabinet or cutout box placed in or against a wall, partition, or other support; and accessible only from the front"? If so, that meets the NEC definition of a panelboard. See Article 100.It has circuit breakers, yes, but it is not your typical panelboard.
A single circuit breaker? No, based on the use of the plural form "automatic overcurrent devices" in the definition of panelboard.What about an enclosed circuit breaker? is that considered a panelboard?
Not a panelboard. Remember dedicated equipment space is for equipment that may require entry after it's already been installed like a panelboard where in the future someone may come in and run new conduits out of the existing equipment. The same wouldn't be true for a single circuit breaker used as an OCPD for a feeder.What about an enclosed circuit breaker? is that considered a panelboard?
No.Went through another thread from 2016.
Splicing in a meter bank
First of all, it is my understanding that the wireway section of a meter bank is considered a panelboard. Based on this, is it OK to splice the SER cable inside the wireway? We've got a 40 unit apartment building and each unit is getting a 1.5 kw PV system. Each unit is metered separately...forums.mikeholt.com
Post #6 seems to say a meter bank is not a panelboard. The meter bank in this thread is Siemens WMM52125RJB... which consists of meters and circuit breakers. Am I reading this wrong?
No, in that I'm not reading it wrong?
Correct the meter bank is not a panelboard and therefore does not require dedicated equipment space.No, in that I'm not reading it wrong?
I agree.Correct the meter bank is not a panelboard and therefore does not require dedicated equipment space.
Some enclosed panelboards have one or more openings for plug-in watt-hour or similar meters. Such panelboards, when marked for outdoor use have, except for the joint between the plug-in meter and opening, been investigated for rain tightness.
To have space above the switchboards, switchgear, panelboards, and motor control centers for conduit / electrical work in the future... that I understand.What is the reason that "switchboards, switchgear, panelboards, and motor control centers" require dedicated space, and does that reasoning apply to meter centers?
That does not rule out being a cabinet. A cabinet just has to have a "frame, mat, or trim in which a swinging door . . . can be hung". So what does the enclosure look like?There are no swinging doors.
If they have breakers they are listed under UL 67Three questions that bear on this topic; sorry I don't have time to research them now:
What is the reason that "switchboards, switchgear, panelboards, and motor control centers" require dedicated space, and does that reasoning apply to meter centers?
If you conclude that the meter center does not meet the definition of panelboard, have you also confirmed it does not met the definition of any of the other 3 items in the list?
And as far as the previous question, what listing standard is the meter center listed under?
Cheers, Wayne