Dedicated Electrical Space

Status
Not open for further replies.

mothball

Member
Location
Eau Claire, WI
No brainer right? 110.26(F)(1)(a)
The space equal to the width and depth ........
..... shall be dedicated to the electrical installation.

Does this mean only conduit from that specific piece of equipment can be in this space or can conduit from any piece of electrical equipmetn be in this space?

I guess what is the commonly accepted/enforced definition of electric installation.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The code is not explicitly clear on this point. I believe that the most common interpretation is that anything electrical can be in the dedicated space, even if it is an conduit that is not related to the panel in question.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The code is not explicitly clear on this point. I believe that the most common interpretation is that anything electrical can be in the dedicated space, even if it is an conduit that is not related to the panel in question.

I agree with Charlie's interpretation.:)

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'd hate to let common sense ever influence my inspections :grin:, but, if you routed a 4" conduit say 12" above a 6" deep can, I might cry foul.
 