ngd4130

Member
Below is the code reference for NEC 110.26. I would appreciate some feedback on this and how it applies to the pictures below. This pipe is a plumbing vent pipe which was installed thru the electrical room. Is this indeed 'dedicated space'? Feedback? :?

picture 010.jpg

picture 011.jpg

picture 005.jpg

picture 003.jpg

picture 001.jpg
 
Last edited:
It is not in the dedicated space required for that panel.

attachment.php
 
Please do not confuse dedicated space (directly above or below the panel vertically) with working space (in front of panel, including above and below panel front height.)
Both are required (although not necessarily in every situation) but the rules are different.

Sent from my XT1585 using Tapatalk
 
Last edited:
Thank you to those who replied! The idea that we have this site to ask questions and bounce them off so many professionals is OUTSTANDING! This makes the electrical standards and the electrical industry even stronger and safer! :cool:
 