So, using that logic, under normal circumstances, nothing special or off the wall, there would be no such thing as an AC "system", meaning a distribution panel, under 150 volts. I have never seen an AC panel with only one buss.
I appreciate everyone's help and advice on this, however, de-energizing the system is a different topic. The original question was to define a "system" of less than 150 volts. Would this be phase to phase or phase to ground? An example of a system is a main AC 120/208 distribution panel feeding multiple branch circuits. So would you consider this under 150 volts or over 150 volts. If anyone thinks it is phase to phase can you give an example, again normal everyday stuff, nothing off the wall, of an AC system less than 150 volts.
After talking with another electrician, he seems to recall the instructor in his NFPA 70e class telling him that if it is not stated phase to phase then it is assumed phase to ground. However he cannot find any documentation to back that up.
Our typical plant panel is considered a 480VAC hazard even when the disconnect and a top mounted transformer are the only devices using 480VAC.
Common to our plant:
Main panel is 480VAC three-phase :: 480VAC system
Sub panel fed 120VAC single-phase from the main panel :: 120VAC system
Sub panel fed 24VDC from either a 480VAC main or 120VAC secondary :: 24VDC system
And just stumbled on it cause I decided to look:
NFPA 70E : 2004 : Article 100 Definitions
Voltage (of a Circuit)
The greatest root-mean-square (rms) (effective) difference of potential between any two conductors of the circuit concerned.
FPN: Some systems, such as 3-phase 4-wire, single-phase 3-wire, and 3-wire direct-current, may have various circuits of various voltages.
Therefore a system of 150V or less would be a system where the circuit with the highest potential was 150V or less. 208/120 would be a 208V system with a 208V circuit and two 120V circuits.