Re: Definition of a Circuit.
My scientific side does not completely understand the N-G separation science. It seems to be a bit of Voodoo logic.
Because this is a very important topic and there may be readers here that are new at this, I think it is important that we do our best to explain it.
Let's try these statements one by one, and see if we are in agreement.
1. The grounded (sometimes neutral) conductor is one of the load circuit conductors. It must be sized to carry load current, which can be continuous.
2. The equipment "grounding" conductor (EGC), (which isn't actually a grounding conductor at all, but that's another story,) is sized to operate the circuit overcurrent device, and is only required to carry the fault current for a few seconds.
3. It (the EGC) is not sized to carry circuit load current, and therefor must be prevented from being in parallel with the grounded load circuit conductor.
4. Because the system grounded (sometimes neutral) conductor, and the equipment enclosures, are permitted to be grounded to the same grounding electrode, they are bonded together at the supply end by the main bonding jumper, so they must be kept isolated from one another thereafter, within the same building.
How are we doing so far? Wayne C, I think you said basically the same thing, in different words.
Ed
[ October 07, 2003, 12:08 AM: Message edited by: Ed MacLaren ]