While studying tables for conductor count in a conduit I'm trying to determine the definition of "conductor" as used in these tables.
Without derating the table calls out "not more than three current carrying conductors". Now, if I run quantity two 250mcm wire paralleled to carry one phase of a three phase setup -- would this be considered one current carrying conductor comprised of two 250mcm wire or would it be considered two distinct current carrying conductors? I think the answer is the former -- two paralleled wires are considered one conductor.
And, to follow, would I then be able to run six 250mcm "wires" (2 paralleled for each phase) through the apropriate conduit without derating. I think the answer to this one is yes, I could run all three phases (three conductors) comprised of a total of 6 wires paralleled two per phase.
Lastly, related to this.. in a 3 phase 4 wire system.. is the neutral considered a "current carrying conductor" for the purposes of this rule? I think the answer is yes.
Thanks
-J
Without derating the table calls out "not more than three current carrying conductors". Now, if I run quantity two 250mcm wire paralleled to carry one phase of a three phase setup -- would this be considered one current carrying conductor comprised of two 250mcm wire or would it be considered two distinct current carrying conductors? I think the answer is the former -- two paralleled wires are considered one conductor.
And, to follow, would I then be able to run six 250mcm "wires" (2 paralleled for each phase) through the apropriate conduit without derating. I think the answer to this one is yes, I could run all three phases (three conductors) comprised of a total of 6 wires paralleled two per phase.
Lastly, related to this.. in a 3 phase 4 wire system.. is the neutral considered a "current carrying conductor" for the purposes of this rule? I think the answer is yes.
Thanks
-J