Here's a source that talks about this from the
Canadian code, FYI.
Thats an interesting 2008 article on Canadian Electrical Code Rule 8-104 Maximum Circuit Loading,
keep in mind that CEC section got revised to harmonize with the NEC. Also we don't use R90 wire or NM-
D cable in the NEC (unless by local amendment like in WA), but we do use the exact same OCPD's.
April 10, 2017 - The 3rd Memorandum of Revision (MOR) is out, and Rule 8-104 is undergoing some significant changes. Subrule (8) has been deleted from the CE
www.ebmag.com
The CEC is written for certain Canadian products and the NEC is also intended for specific US products (we still use imperial pipe sizes and AWG wire). They are not totally harmonized (yet).
Go to the NFPA web site and search past NEC issues until you find the one where the "continuous load" definition first appeared, then search the ROP's, you may find what you're looking for
That would be 1965 but prior to that they used the term
‘long periods of time’ which was not well defined, the first mention of that would be the 1951 NEC 2125(b)
“the total load shall not exceed the branch circuit rating, and shall not exceed 80 percent of the rating where in normal operation the load will continue for long periods of time such as store lighting and similar loads”, similar verbiage later in 1959 for feeders.