Definition of Feeder
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
Here is a proposal I am thinking of making
Feeder.
All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device. Where these conductors are feeding an individual piece of equipment such as hot tubs, motors, etc.then the conductors shall be considered branch circuits.(CMP-2)
Here is my substantiation. I am not a good writer and would love some input on my proposal and maybe some help in re-wording my substantiation.
There are different rules for feeders and branch circuits but in some cases the conductors from a panel that feed a hot tub, air condition etc and have a fused disconnect are really branch circuits all the way to the equipment but by definition, these conductors are called feeders to the fused disconnect and branch circuits to the equipment. Whereas, if the same setup had an unfusd disconnect then the entire run would be a branch circuit. I feel it is unnecessary to treat the conductors from the panel to a disconnect differently just because one unit has a fused disconnect and the other does not.
kwired
Electron manager
NE Nebraska
I like the general idea, I don't know how to submit it, but I think that for the hot tub or HVAC application it should be supplying either factory installed overcurrent devices in the equipment or an individual over current device used primarily as a local disconnecting means.
If you supplied a small loadcenter next to an AC unit and supplied the AC unit as well as the receptacle that is required to be near the unit from that loadcenter - I think it should still be considered a feeder. But if you only supplied multiple breakers factory installed or as part of listed accessories for that HVAC equipment (like an air handler with add on heat strips often have) I think that should be considered a branch circuit.
Dennis Alwon
Chapel Hill, NC
If a receptacle is added then I doubt they (cmp) would go for it. The overcurrent protective device inside the unit is a supplemental overcurrent protective device and, as such, would not change anything. The problem is when you have the 2 breakers in a disconnect feeding the unit. In that case, I would consider that as applicable in what I wrote because it still only feeds one unit.
al hildenbrand
Minnesota
Electrical Contractor, Electrical Consultant, Electrical Engineer
Feeder.
Because of the Article 100 Definition of Service Equipment, I see your proposal causing a difficulty when there is a subpanel between "hot tubs, motors, etc." and the Service Equipment . . . a conflict arises as to what the conductors between the "Service Equipment" ("connected to the load end of the Service Conductors") and the subpanel are called.
We would normally think of the Service Equipment to subpanel conductors as a Feeder, but your proposed change, because of "All circuit conductors" in the Feeder definition, makes them a "Branch Circuit."
kwired
Electron manager
NE Nebraska
I think existing feeder definition is fine, if anything to get what Dennis wants to accomplish done a modification may be needed to the branch circuit definition.
Otherwise you have service conductors and branch circuit conductors, and everything else is a feeder or a feeder tap.
Dennis Alwon
Chapel Hill, NC
I don't get it... Any feeder is from either a service or the sub panel as it stands now. Why does my words change that... The definition does not affect the wires between the service and a subpanel-- those are still feeders-- it only changes when it feeds an individual piece of equipment
al hildenbrand
Minnesota
Interesting point.
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
Ignoring the other three Article 100 Definitions involving "Branch Circuit . . .", adding something here about the next OCPD, if not being in Service Equipment, being the Branch Circuit.
petersonra
Northern illinois
engineer
I don't see the purpose of your change.
Feeder. All circuit conductors between the service equipment,
device.
The final branch circuit rated OCPD is still where the branch circuit starts.
al hildenbrand
Minnesota
Your proposed wording says "Where these conductors" and that refers to the original opening words "All circuit conductors" which, when there is a subpanel, includes the Service Equipment to subpanel feeder.
You are not directly addressing the individual utilization equipment with a local disconnect that has OCPD included. Your words in the proposed change don't directly say the final OCPD is not the OCPD in the local disconnect. And, more importantly, if the ignored actual final local disconnect OCPD is coming from a OCPD NOT in the Service Equipment, that this subpanel located OCPD is to be the "final OCPD" at the beginning of the Branch Circuit.
Dennis Alwon
Chapel Hill, NC
Yes but the proposal has an exception when there is an overcurrent protective device in between the load center and a piece of equipment only then I want that normally called feeder to be called a branch circuit. Thus the entire run between a panel and a single piece of equipment is a branch circuit whether there is a disconnect with overcurrent protective device in it or not
Dennis Alwon
Chapel Hill, NC
Yes but it doesn't effect those conductors because they are not feeding an individual piece of equipment-- maybe I should say utilization equipment
You are not directly addressing the individual utilization equipment with a local disconnect that has OCPD included. Your words in the proposed change don't directly say the final OCPD is not the OCPD in the local disconnect. And, more importantly, if the ignored actual final local disconnect OCPD is coming from a OCPD NOT in the Service Equipment, that this subpanel located OCPD is to be the "final OCPD" at the beginning of the Branch Circuit.[/QUOTE]
I agree that the definition needs to be cleared up a bit.
For example, I have a cable from my breaker panel to a fused SSU that supplies power to my furnace. There is a cable going from the SSU to the furnace.
Is the cable running from the breaker panel to the SSU a feeder or a branch circuit conductor? What if I change from a fused SSU to a non-fused switch located at the same place?
Smart $
Esteemed Member
Ohio
I've tossed the idea around in my mind for a little bit and keep arriving at the same conclusion... :happysad:
Perhaps the change should be based on whether the 'feeder' conductors can support a greater load than the single piece of utilization equipment they supply, i.e. 'feeder', versus barely enough to support the connected single load, i.e. 'branch'.
Better hurry if you want to get this refined to an accept in principle level. :happyyes:
al hildenbrand
Minnesota
Actually, no, there is no exception as written. Your proposed language is added as part of the actual Definition of the Term "Feeder".
And you never mention "load center" in your language.
More importantly, if there are TWO or MORE OCPDs between the Service Center OCPD and the individual utilization equipment, how do you determine which is the beginning of the Branch Circuit as you are "excepting?"
al hildenbrand
Minnesota
Great examples.
By the 2017 NEC Definitions in Article 100, the fused switch (SSU) is on the end of a Feeder. A non-fused SSU is IN the Branch Circuit.
Marky, for the purposes of running the cable or raceway method to your furnace, does calling the wiring method a Feeder change anything?
Dennis Alwon
Chapel Hill, NC
Great examples.
That is the exact example I made in my statement of substantiation
Dennis Alwon
Chapel Hill, NC
Great examples.
In some cases in can change the size of the now feeder conductor. The feeder would be larger than the branch circuit. We had a thread on it a while ago
al hildenbrand
Minnesota
My question to Marky is specifically about his furnace . . . I am assuming he is describing a 15 Amp 120 Volt supply to a normal residential forced air furnace. . . maybe it is a hydronic boiler or a steam boiler, same 15 Amp 120 Volt supply. How does calling the wiring to the fused disconnect on the side of the furnace a feeder change anything?
And about that thread. . . do you recall the link?
Yes, that is correct.
I also have a fused SSU that supplies power to the receptacles on my work bench. Just for definition's sake, is the cable that goes from the panel to the work bench SSU a feeder, or is it a branch circuit conductor, or maybe even both?
al hildenbrand
Minnesota
:D The conductors coming to the work bench SSU, when fused, are Feeder conductors. The conductors between the fuse LOAD side terminal and the Outlet are the Branch Circuit. The SSU is the "final OCPD."