geoff mickelson
Member
Mike: I am having an issue with an electrical engineer he is telling me that a main distribution panel and metering device must be phyically mounted on the commercial building (church) or the feeder panels and the feeder panel conductors would be considered service enterance, therefore because there 2 distribution panels in the building he is saying if the MDP and metering is mouted off the building but still on the church premise we would be required to run only 1 conduit into the building feeding 1 400amp panel and subbing to another 200amp. He is saying that if we run run 2- 2inch conduits from the MDP to feed 2- 200amp panels in the building that would constitute 2 services into building, he says that it is a NEC code issue and I do not agree as per NEC. If there is an issue with "those having jurisdiction" then those having jurisdiction should have some type of written amendment to the NEC. Is that correct? I am working in Maui county Hawaii Thank-you Geoff Mickelson Kihei, Hi