(F) Unit Equipment. Individual unit equipment for emergency illumination shall consist of the following:
(1) A rechargeable battery
(2) A battery charging means
(3) Provisions for one or more lamps mounted on the equipment, or shall be permitted to have terminals for remote lamps, or both
(4) A relaying device arranged to energize the lamps automatically upon failure of the supply to the unit equipment
The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.
slong100 said:I guess my real question is: if you have installed an emergency battery pack within a 2x4 fixture, then does it label that entire fixture as unit equipment. Then in this case, would we have to label the circuit accordingly? If this were the case, then just every circuit with emergency battery packs would need to be labeled. This could impact every lighting circuit?
The plans reviewer wants you to change your panel schedules as per this:?slong100 said:I guess my real question is: if you have installed an emergency battery pack within a 2x4 fixture, then does it label that entire fixture as unit equipment. Then in this case, would we have to label the circuit accordingly? If this were the case, then just every circuit with emergency battery packs would need to be labeled. This could impact every lighting circuit?
If thats the case why don't you change the name of those cirs. from Lighting to Lighting/EM Lighting?The branch circuit that feeds unit equipment shall be clearly identified at the distribution panel.