Substantiation:
This change to the 2005 edition of the code should never have been accepted. There was no technical substantiation.
Are there any documented cases of this being a problem?
Where did 12? come from? Is 11? unsafe? Is 12?1? safe?
Also, this requirement is so vague in its language that it is impossible to create uniform interpretation. What is to bonded together here? The generators? The attractions? The rides?
How do I bond them? 500Kcmil copper? 6 AWG? What portions of Article 250 apply? Do I base the size on 250.122? Do I use Table 250.66?
What happens when a voltage is imposed from one system (during a fault) to the metal, non-current carrying parts of the other system and its rides and attractions? Why are we energizing attractions that were safe until we bond them to something that is under fault? Isn?t isolation safer than bonding? I don?t want to be touching a ferris wheel that is perfectly safe, only to get shocked because a different generator had a fault and imposed its voltage on me for the time duration of the overcurrent device to open. I would rather just not get shocked! Isolation is the answer, not bonding.
I urge the members of Panel 15 to delete this proposal that never should have passed in the first place.
This change to the 2005 edition of the code should never have been accepted. There was no technical substantiation.
Are there any documented cases of this being a problem?
Where did 12? come from? Is 11? unsafe? Is 12?1? safe?
Also, this requirement is so vague in its language that it is impossible to create uniform interpretation. What is to bonded together here? The generators? The attractions? The rides?
How do I bond them? 500Kcmil copper? 6 AWG? What portions of Article 250 apply? Do I base the size on 250.122? Do I use Table 250.66?
What happens when a voltage is imposed from one system (during a fault) to the metal, non-current carrying parts of the other system and its rides and attractions? Why are we energizing attractions that were safe until we bond them to something that is under fault? Isn?t isolation safer than bonding? I don?t want to be touching a ferris wheel that is perfectly safe, only to get shocked because a different generator had a fault and imposed its voltage on me for the time duration of the overcurrent device to open. I would rather just not get shocked! Isolation is the answer, not bonding.
I urge the members of Panel 15 to delete this proposal that never should have passed in the first place.