Yes the machine is European. The transformers came with it. There are (3) dry type transformers that go from 240 to 380. This is for the main 100 amp feed to the press. There are ink dryers that I am told are 240 volt , 3 phase center grounded, 60 amp.
Thanks
If the front end supply of the machine is a 240 to 380 transformer, most likely all it needs is 240 volts with three lines that have a 120 degree phase angle between them (grounded or ungrounded) and it will work fine.I agree for the most part. Thing is there are people that work on these presses for a living. That's the guy you want to talk to.
No. No buck/boost. I have not worked on a lot of presses so I do not fell comfortable giving a lot of advice about them but my experience has been isolation transformers are SOP for changing voltage from 208 to 240 or even going from 240 to 240 then on to the machine.
Sounds like the last place it was connected to had a 240 delta supply with a mid point ground on one phase. Doesn't necessarily mean it can only be connected to that type of source, especially if there is no "neutral" required from the supply circuit.
Chances are the 240 to 380 transformer was added on whenever this thing was initially installed in the US. If installed in a place that has a 380/220, 400/230, 415/240 system, it would probably direct connect to it.
If OP does not have the transformer as the "front end" of the supply to the machine, we probably need more details to be of much help.