CTs are connected in star on T/F delta connected winding side & in delta on T/F star connected winding side for T/F differential protection and the reason
is to eliminate zero sequence current for avioding the differential relay from operating.but i am confused when we say that the Wye connected formula is
Iline=Iphase and Delta connected formula is Iline = 1.73 * Iphase
so if these formulas are applied ,then will this actually effect the current value of the secondary CT there by activating the differential relay. Thanks in advance