Can a 120/240 two pole breaker be used on a ungrounded 240v delta system? Or does in need to be straight rated.
The UL White Book states that, "2-pole circuit breakers suitable for controlling 3-phase, corner-grounded delta circuits are marked 1? - 3? to indicate their suitability." However, if it were switching the neutral, a normal but full voltage rated 3-pole circuit breaker could be used.. . . and more importantly it also needs to be rated for use on Grounded-B phase systems. . .