There is a delta 480v to 240v transformer being installed at the project I am on. They did not ground one of the phases and it is not an ungrounded system.
Is there an application where it is okay not to ground the B phase? Just curious.
There are a very limited number of possibilities here:
1. The output winding is a high leg delta, in which one of the 240 windings is center tapped and the center tap is grounded.
2. The output windings are simple delta, and one of the three corners is grounded. It need not be the B phase, but that is customary.
3. The output winding is totally ungrounded, with the whole set of windings free to float at any voltage with respect to ground while maintaining a constant 240V from terminal to terminal.
There is no way that it could be grounded other than 1 or 2.
However, in the case of 3, the output terminals may not
appear to be ungrounded.
There will be a certain amount of capacitance between each winding and ground, and between the wires connected to the secondary and ground.
These capacitance values will be roughly equal under normal circumstances, so they form a wye voltage divider of capacitors with the center point firmly grounded. (The raceways and the transformer shell are grounded.)
That means that if you use a high input impedance meter to measure between phase terminals and ground you will get approximately 137V on each of the three.
But that 137V cannot sustain a load, because of the high impedance of the stray capacitors. That means that if, for example, you connect a 240 or even 130V light bulb from A, B or C to ground it will NOT light.
If you allow for the effect of connected loads, it is also possible that one of them could also have the effect of trying to center the delta with respect to ground, and even allow more current to be measured.