There is a delta 480v to 240v transformer being installed at the project I am on. They did not ground one of the phases and it is not an ungrounded system.

Is there an application where it is okay not to ground the B phase? Just curious.
 
There is a delta 480v to 240v transformer being installed at the project I am on. They did not ground one of the phases and it is not an ungrounded system.

Is there an application where it is okay not to ground the B phase? Just curious.

Well if they did not ground one of the phases, then it IS an ungrounded system (unless it has a center tapped winding that is grounded). IF it does not have center tapped winding, you may leave it ungrounded but you would need fault detectors. For most general applications, I would say it is simplest to corner ground it.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
There is a delta 480v to 240v transformer being installed at the project I am on. They did not ground one of the phases and it is not an ungrounded system.

Is there an application where it is okay not to ground the B phase? Just curious.

There are a very limited number of possibilities here:
1. The output winding is a high leg delta, in which one of the 240 windings is center tapped and the center tap is grounded.
2. The output windings are simple delta, and one of the three corners is grounded. It need not be the B phase, but that is customary.
3. The output winding is totally ungrounded, with the whole set of windings free to float at any voltage with respect to ground while maintaining a constant 240V from terminal to terminal.

There is no way that it could be grounded other than 1 or 2.

However, in the case of 3, the output terminals may not appear to be ungrounded.
There will be a certain amount of capacitance between each winding and ground, and between the wires connected to the secondary and ground.
These capacitance values will be roughly equal under normal circumstances, so they form a wye voltage divider of capacitors with the center point firmly grounded. (The raceways and the transformer shell are grounded.)
That means that if you use a high input impedance meter to measure between phase terminals and ground you will get approximately 137V on each of the three.
But that 137V cannot sustain a load, because of the high impedance of the stray capacitors. That means that if, for example, you connect a 240 or even 130V light bulb from A, B or C to ground it will NOT light.
If you allow for the effect of connected loads, it is also possible that one of them could also have the effect of trying to center the delta with respect to ground, and even allow more current to be measured.
 

GLSA

Member
Location
Ut
Since they didn't ground it, what are the possible dangers for personal and equipment besides a ground fault not being cleared?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Since they didn't ground it, what are the possible dangers for personal and equipment besides a ground fault not being cleared?
Certain types of arcing ground faults can pump up the delta to twice or more the nominal voltage with respect to ground. This could be more than the insulation in some wiring, distribution equipment and loads can tolerate.
Also, someone expecting no more than 137V to ground could be exposed to 480V to ground or more.
 