Obviously, the POCO must approve the connection (some will not allow a PV system to connect to the B phase), but it is a small-ish PV system that would load the transformer bank with only 5.8kVA per phase if there are no loads.Is this a standard utility open delta bank / service?
Or a closed delta?
Sorry, I do not know where my math went south, but obviously a 30kW inverter even through a transformer will load the utility transformer bank by a maximum of 10kVA per phase. Pesky sqrt(3)!Obviously, the POCO must approve the connection (some will not allow a PV system to connect to the B phase), but it is a small-ish PV system that would load the transformer bank with only 5.8kVA per phase if there are no loads.
Where is that 0.867 coming from?For an open delta service would it be something like
30kVA/.867 = 34.6kVA
34.6/2 = 17.3 kVA each?
It is used with open delta configurations.Where is that 0.867 coming from?
It come fromWhere is that 0.867 coming from?
It's sqrt(3)/2, and applies to balanced 3 phase loading on an open delta.Where is that 0.867 coming from?