coulter said:dnem -
My comment was that I have never seen a corner grounded 240D. Has anyone else ever seen one? If so, I'd be curious why it was speced that way. The only time I ever see 240 D is for specific loads like K2500 posted.
K2500 -
Was the one you refered to a corner grounded 240D, 240V high leg grounded D, or un-grounded 240D?
dnem said:... 1] Only need one voltage
I don't know what that means. There is only one voltage - 3 phase 240V delta. Corner grounded or not, that is the only one there is.
What it means all depends on what?s being compared.
Comparing 3? corner grounded delta to 3? floating [ungrounded] delta, both have only one voltage.
Comparing 3? delta to 3? wye, delta has one voltage, wye has 2. . My comment wasn?t focused only on just different types of deltas.
coulter said:dnem said:... 2] Smaller cheaper transformer ...
I don't see that either. I've never heard of a transformer mfg making a different transformer for corner grounded D as opposed to ungrounded D.
Once again my comment wasn?t focused only on just different types of deltas. . When you take a certain size transformer enclosure and wind a specific amount of insulated copper in its windings, you?ll get more KVA out of it if you configure it as a delta. . You need a bigger enclosure and more copper for the same KVA wound wye. . That was my only point.
coulter said:dnem said:... 3] Don't need ground detectors
That's true, But the cost of three transformered 240V pilot lights isn't much.
carl
If because of the single voltage, cheaper transformer reasons you choose delta instead of wye, then a corner grounded will operate the same as a floating delta. . The floating gives you the option of continued operation after the first fault. . The corner grounded is safer in some ways.
Most of the delta secondarys that I see are center tapped/high leg types. . Of the remainder, I see many more corner grounded than floating. . I?ve actually only seen 2 floating delta systems during inspections. . Most of my exposure came from my brother-in-laws floating delta in his machine shop.
I?ve got a ?rare bird? for you.
Have you ever seen a corner grounded system that uses the building steel as the corner grounded phase itself ? . It has 2 wires in a steel conduit [the combination of building steel and conduit functions as the 3rd phase / grounded phase]. . No fault current only equipment ground anywhere. . Each motor case has a bond wire to the building steel. . It was installed during WW2.
David