Delta transformer
BTE
Hello everyone,
My question is: Utility 3 phase Delta transformer 480 volt secondary with out a neutrel (three single transformers pole mounted). Readings inside building electrical system are Phase A to B to C all 480 volt phase to phase. Phase to ground is Phase A zero volts, Phase B & C to ground are 480 volts. All equiptment and lighting in building is functional. I found information in a electrical book that at times but not often the secondary side of a open or closed Delta transformer will have one phase connection grounded. It is one method of grounding the secondary of a Delta Bank.
Is there a problem with this system?
Are there any safety issues?
Are there any cost effective alternatives?
Hope to read you responce.
Thanks, BTE
Delta Transformer corner grounded.
Hey Chris,
Are there any problems with a Corner Grounded Delta three phase system?
No Problems. But you must use fullky rated 480v OCPDs not those rated 277/480v and a SE panel suitable and listed for a 480v grounded B phase.