LarryFine said:
No, if you have a 6-lead 480v motor, you have the option of 240v or 480v, but it will remain wye or delta. A 9-lead motor is actually a 12-lead motor with one connection point inaccessible.
To switch a motor between wye and delta, you need all of the winding ends individually accessible, which means it will be a 6-lead, single-voltage motor, or a 12-lead, dual-voltage motor.
Let me summarize what I think I understand
1) If I have a 3 lead motor I do not care weather it is wired for wye or delta.
For instance if I have a 480V motor then I dont care how its wired, and if
its wired in a wye configuration then although the voltage across the coils
will only be 58% the motor manufacturer has already accounted for this
for the motors proper operation.
2) If I have a 6-lead dual voltage motor, such as 480/240 for example then it
will be either delta for both voltages, or wye for both voltages and is not
meant to be swapped between delta and wye for different voltages.
3) If I have a 6-lead single voltage motor such as a 480V motor then there is
an option weather to wire it for wye or delta. There is also an option for
wiring this type of motor for a wye-start, delt-run configuration. You have
to keep in mind however that in the wye configuration there will only be
58% of the voltage across the coils. What is a case where I would want
to run a motor in the wye configuration with a particular system voltage
avaliable?