Which is a better option for the primary of a power transformer?
General question .... general answer .....
Delta primary is best
Thanks! This is a power transformer, 115kv to 33kv. Basically the debate is between a delta or wye primary.
I've studied that at higher-voltages (above 30KV) delta-wye transformers are more susceptible to ferroresonance, which is why some utilities use wye-wye. But I doubt that's the only reason.
That's true, however ferroresonance is only a problem with single pole tripping devices (i.e. fuses) on the delta winding. If a 3 phase tripping device (breaker, recloser, etc.) is used with a delta primary ferroresonance is not a concern. Even if we're not concerned with ferroresonance, if we want to use fuses for primary protection think about the fuse response to a ground fault. Depending on the location in the winding, a fuse may not see a ground fault on a delta winding or it may have a slow response. A wye primary will allow the fuses to operate faster resulting in less damage to the transformer and faster clearing, meaning a shorter voltage sag for other custoemrs on the line.
All of that being said, any medium to large industrial service should have a delta wye transformer to segregate utility ground protection from plant ground protection, and it should be equipped with a 3 phase primary tripping device to better protect the transformer.