Ok haven't posted in awhile and scratching my head on this one. Looking for insight
I have a 120/208 3 phase delta input step up transformer with 230/380volt Y output.
Here are my current readings which looks good:
Input:
X1-G 116v
x2-G 115v
x3-G 116v
X1-X2 201v
X1-X3 201v
x2-X3 200v
Output:
H1-H0 212v
h2-H0 216v
H3-H0 213v
H1-H2 370v
H1-H3 366v
H2-H3 370v
Here is my issue, keep in mind I currently do not have any load wires landed on the transformer yet. When energizing the transformer with test leads connected to X1-X3 I get a reading of 97 volts for about 1 minute and then the voltage corrects itself. Same on X2 except the reading is about 112volts. I verified the issue is not the breaker as I took the leads off the transformer and did not experience this issue. After about a minute all reading are correct.
Any thoughts on why the input leads on the transformer have a lower voltage initially?
I have a 120/208 3 phase delta input step up transformer with 230/380volt Y output.
Here are my current readings which looks good:
Input:
X1-G 116v
x2-G 115v
x3-G 116v
X1-X2 201v
X1-X3 201v
x2-X3 200v
Output:
H1-H0 212v
h2-H0 216v
H3-H0 213v
H1-H2 370v
H1-H3 366v
H2-H3 370v
Here is my issue, keep in mind I currently do not have any load wires landed on the transformer yet. When energizing the transformer with test leads connected to X1-X3 I get a reading of 97 volts for about 1 minute and then the voltage corrects itself. Same on X2 except the reading is about 112volts. I verified the issue is not the breaker as I took the leads off the transformer and did not experience this issue. After about a minute all reading are correct.
Any thoughts on why the input leads on the transformer have a lower voltage initially?