mslowley
Member
- Location
- Marion, NY
I'm looking for clarification on the following.
Our facilty checked GFCI's this past month and discovered several circuits failed the test. All of them originate in the same 208Y/120 VAC panel supplied by a 480 Delta - 208Y/120 transformer nearby. Upon inspection I see no bond between the neutral and ground bars. This concerns me because the test was conducted using a handheld device (Greenlee) for the purpose, those same circuits are GFCI breakers in that panel and the test button on each of them trips the circuit 100% of the time. If GFCI's work by comparing current out vs. in, why does the breaker test button trip and not when there is a load test conducted? Once we bonded the X0 to Ground, no more problems.
Our facilty checked GFCI's this past month and discovered several circuits failed the test. All of them originate in the same 208Y/120 VAC panel supplied by a 480 Delta - 208Y/120 transformer nearby. Upon inspection I see no bond between the neutral and ground bars. This concerns me because the test was conducted using a handheld device (Greenlee) for the purpose, those same circuits are GFCI breakers in that panel and the test button on each of them trips the circuit 100% of the time. If GFCI's work by comparing current out vs. in, why does the breaker test button trip and not when there is a load test conducted? Once we bonded the X0 to Ground, no more problems.