ok, as I am also a student trying to learn, I notice several things here. It is a church. So, lighting demand... Constant for the last lighting load as that would be the signage outside..
Ventilation..ie fans.. not under lighting normally. Would not usually be considered constant in a church, unless the church is used all week as well.
R/ In this case, the fans are going to be woking more than 3 hours, that is the reason that i consider them a continuos load, 125%.
Cooking... unless this is running a daily soup kitchen would probably be minor. so not part of major load.
R/ Applying the demand factor for electric ranges (NEC TABLE 220.55) it would be at 100% 8000VA.
Altar circuit.. Assuming this is for sound system etc, but still, usually not considered a constant load but occasional load.
In fact, with the exceptions of the Pastor and the Secretary offices, most of the rest of the circuits are usually considered occasional circuits and the load is usually for vacuum cleaners.
Lavatory Circuits.. Both bathrooms may be on same circuit unless you have those fancy hand dryers in them... those require dedicated circuits according to the manufacturers, for no more than two of them per circuit, or at least the ones I am used to are rated that way.
Your local authority will probably change the kitchen circuits from one to three... refrigerator, and two for outlets.. plus a stove if you have one, or a microwave circuit if you have one of those.
R/ yes I have one, sorry the language (Circuito de toma dedicado para Microondas= dedicated circuit for Microwave)
Most of the churches I have dealt with, the local authority used the residence requirements for the kitchens... but check on that.
only gear here that counts for full load is stove and fridge... you listed the microwave but not in the kitchen...
again, the separation of circuits... cocina and microondas are both kitchen only... you list classrooms... so, would need more information on number of classrooms etc...
R/ There are about 8 classrooms, and there are a mimimum of 3 outlets per room, so when you add all the outlets the result of the operation is less to 10000VA, then, all this would be at 100% (nec table 220.44), again connected load= demand load.
but, it is a decent start. Just, people on here will have trouble helping because they need more information... That is before you correct the load errors in your calculations.
Note that i need to check on... If you have classrooms, because they use the lights for more than three hours, the lighting load becomes constant, i think... But I may be wrong on that.. time to go double check my code books.