Demand Factor, Auto Dealer + Repair Shop Design.

VENgineer

Member
Location
Miramar Fl
Occupation
Electrical Engineer
Good afternoon, I hope you can help me. I can't find any information about which demand factor I can use for calculating the service feeder, considering the occupancy type (Auto Dealer with service, No EV Chargers). The total connected load is 490kVA, mostly air conditioning, 280kVA.

The system is VRF, so it's quite efficient and will never consume all the equipment at maximum capacity.

Could you guide me a little in this situation?

Thank you in advance
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
There is no demand factor that you can apply. Connected load is connected load. The only demand that we have is in the receptacle load and that is not that much help.
 
Top