Demand factor for cooktops

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you thinking of Article 220 calculations? This is from T220.55.

Table 220.55 Demand Factors and Loads for Household Electric Ranges, Wall-Mounted Ovens, Counter-Mounted Cooking
Units, and Other Household Cooking Appliances
over 1 3 ? 4 kW Rating (Column C to be used in all cases except as otherwise
permitted in Note 3.)
 
Status
Not open for further replies.