Thanks for the effort, Ekhlas. But you will allow me to observe that that spreadsheet was custom-designed for a project in your locality. The voltage levels are 380 phase to phase, and 220 phase to ground. The spreadsheet tabs are related to specific buildings and panels. The content of the various tabs includes specific equipment in your buildings that may not apply to other buildings in other projects. Therefore, the work that would be necessary to adapt the spreadsheet to other voltage levels and other project configurations would be prohibitive.Click below link and find out the excel sheet. It may help you.
Thanks for the effort, Ekhlas. But you will allow me to observe that that spreadsheet was ----------use in any of my projects.![]()
Not sure if it would matter from a load calculation standpoint, but its also for use with 50 htz power...
...This being a salon, it is possible that the receptacle load will be more than the load calculation takes into account.
The space is obviously pretty small - probably around 1250 square feet considering the lighting and HVAC loads. With a receptacle load of 15.48 kVA, that would equate to basically 86 "convenience receptacles" which would be highly unlikely in a tenant space this small.
And as Charlie said, the circuit breaker only needs to be rated to carry 125% of the continuous load plus 100% of the noncontinuous load after demand factors have been applied.
I'm sure I'm going to get blasted for this but why would the OP place a 125% demand factor on the lighting load? Table 220.42 states that the demand factor for this type of occupancy to be 100%.
I would agree with your statement here, however, your quote does not match what was written. What was written is quoted as follows:
"More to the point, we are allowed to load the breaker to a total of (125% of the continuous" PLUS (100% of the non-continuous). "
Those two statements are NOT saying the same thing, hence why I asked where did Charlie derive that from.
Please see my reply in post #31. The code sections referenced in that post give the requirements for sizing the service and feeders conductors respectively. NEC 240.4 requires conductors to be protected in accordance with their ampacities with a few exceptions. Therefore, if the service conductors or feeders are rated at 125% of the continuous load plus 100% of the noncontinuous load, the OCPD can not exceed the ampacity of the conductors unless the installation falls under NEC 240.4(A) through 240.4(G).
I'll be more clear, in post #6, it was stated you can load the breaker to 125% of continuous plus the non-continuous, i.e. you would be overloading the breaker in this case, or undersizing it, whichever point of view you want to take. Thanks for your help, although I am aware of the loading requirements, I was trying to get the poster of post #6 to realize the error without being too rude about it.
Apparently, they chose not to address the issue, although I imagine it was a just a misplaced word or two.![]()