BatmanisWatching1987
Senior Member
- Location
- NJ
- Occupation
- Jr. EE
The apartment is about 900 Square Feet and everything is Electric (Stove/Range, Electric Hot Water, HVAC System)
Service is 120/240V/1 Phase
If I convert it to AMP, I get about 165 AMP.
What type of demand factor do you guys use for a single apartment to reduce the load?
Service is 120/240V/1 Phase
Equipment | AMP | Load |
Range | 40- 2 Pole | 6,000 VA |
Electric Hot Water | 30- 2 Pole | 4,500 VA |
HVAC: CU-1 | 30- 2 Pole | 4,500 VA |
HVAC: AHU-1 | 20- 2 Pole | 3,000 VA |
HVAC: Electric Heat Pump | 60- 2 Pole | 10,000 VA |
2 Kitchen Outlet | 20 (2x) | 3,000 VA |
Fridge | 20 | 1,500 VA |
Dishwasher | 20 | 1,500 VA |
Hood/Microwave | 20 | 1500 VA |
Bathroom: Lights/Recep/Fan | 20 | 1,000 VA |
Receptacle | 20 (2x) | 3,000 VA |
Total | 39,500 VA |
If I convert it to AMP, I get about 165 AMP.
What type of demand factor do you guys use for a single apartment to reduce the load?