Demand Load for Apartments

Status
Not open for further replies.

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
The apartment is about 900 Square Feet and everything is Electric (Stove/Range, Electric Hot Water, HVAC System)
Service is 120/240V/1 Phase

EquipmentAMPLoad
Range40- 2 Pole6,000 VA
Electric Hot Water30- 2 Pole4,500 VA
HVAC: CU-130- 2 Pole4,500 VA
HVAC: AHU-120- 2 Pole3,000 VA
HVAC: Electric Heat Pump60- 2 Pole10,000 VA
2 Kitchen Outlet20 (2x)3,000 VA
Fridge201,500 VA
Dishwasher 201,500 VA
Hood/Microwave201500 VA
Bathroom: Lights/Recep/Fan201,000 VA
Receptacle20 (2x)3,000 VA
Total39,500 VA

If I convert it to AMP, I get about 165 AMP.

What type of demand factor do you guys use for a single apartment to reduce the load?
 

topgone

Senior Member
I usually see it at 8kva. But I reduced it down to 6kVA with about a 80% demand factor.

If the range is not over 12 kW, you are allowed to put 8 kW as the demand (Column C). Other ratings below, you use what's specified demand factor in Table 220.55. What really is the range load?
 