When he finally rents the space, is he going to tell tenant A, "Sorry, we're going to be interrupting your power at unpredictable intervals to hook up someone else who hasn't been generating a steady income stream for us"?Ok now the owner is saying they would disconnect demo all branch circuit in one of the spaces and keep branch circuits to other tenant where panelboard is.
So the other tenant space would not have any power or light.
I guess that would make it compliant?
Space B is unoccupied.If the space "B" is leased, it needs it's own panel. Presumptively, the owner had the work done to be in compliance with the NEC, said work not having been permitted or inspected.
ExactlyEven if they have their own panel in the second space, if nobody is leasing it, they will not have a meter in anyway, so there will be no power anyway. The most I can see being done is any power that would go through the demising wall would be disconnected.(short of landlord power such as security lights, alarms etc) The new tenants in that space may want a bigger service anyway, and would be addressed with the buildout permit when that time comes.
I was talking about after he finally leases space B. Sorry for the confusion.Space B is unoccupied.
This is a common occurrence in retail spaces. They get carved up all the time.
He needs a building permit which will assist you in determining utilities required
2105 IBC
SECTION 105 PERMITS
[A] 105.1 Required. Any owner or owner’s authorized agent who intends to construct, enlarge, alter, repair, move, demolish or change the occupancy of a building or structure, or to erect, install, enlarge, alter, repair, remove, convert or replace any electrical, gas, mechanical or plumbing system,
the installation of which is regulated by this code, or to cause any such work to be performed, shall first make application to the building official and obtain the required permit.
The code does not make it confusing. There is no reason for you to be the least bit concerned about unoccupied space in a building. There is no tenant in space B. Even if there were a tenant in space B there is no code violation if space B's breakers are in space A as long as both tenants can access them. A locked door does not violate the requirement for breakers to be readily accessible. It may be a bad design, it may be inconvenient, but it is not a code violation. There is, however, no need to have that discussion because there is only one tenant.Yes and building permit was received. I happen to be electrical building official for AHJ in this case but code makes it confusing that’s all. See post #1
If the landlord decides, for example, to use the unleased space for storage while waiting for a tenant, then I would say that space B becomes occupied. But if the landlord maintains access rights to space A it would not create a code problem. JMOThe code does not make it confusing. There is no reason for you to be the least bit concerned about unoccupied space in a building. There is no tenant in space B. Even if there were a tenant in space B there is no code violation if space B's breakers are in space A as long as both tenants can access them. A locked door does not violate the requirement for breakers to be readily accessible. It may be a bad design, it may be inconvenient, but it is not a code violation. There is, however, no need to have that discussion because there is only one tenant.