Dennis Alwon said:So why bother running the extra conductors unless you plan for the derating.
Well we do not know that the additional conductors will be current carrying conductors.
Dennis Alwon said:So why bother running the extra conductors unless you plan for the derating.
haskindm said:If they are being installed just to meet a requirement of the plans, I would not count them as current carrying conductors as the probability is that they will never be used.
frizbeedog said:Wait...that's the next guys problem. Either way, you're the next guy, and it's a problem.:grin:
iwire said:So how much money do you give away when not required to?
haskindm said:The only reason I could see for installing "spare" conductors, would be that the plans/specifications call for them. Otherwise it would be like sticking dollar bills in the conduit before leaving the job... If they are being installed just to meet a requirement of the plans, I would not count them as current carrying conductors as the probability is that they will never be used.
"make it easy for the next guy."
You are confusing minimum code requirements and good design practice. I agree that if I put spares in a conduit, it is a good idea to size the conductors under the presumption that all will be current-carrying some day. When that future install is done, the owner will be happy that I made that precautionary extra step. But the code does not require me to do it, and the code does not care if the owner is happy.Local26 Sean said:If you pull extra conductors into a raceway, haven't you already decided that they will carry current at some point?
Local26 Sean said:If you pull extra conductors into a raceway, haven't you already decided that they will carry current at some point?
The ability of insulated wire to carry rated current is dependent on the temperature of said insulation. That is, as current increases through a conductor it gets warmer, and that heat is dissipated through the insulation. When the temperature of the insulation is at it's rating, it begins to degrade... and higher temperatures make it degrade perhaps at an exponentially faster rate.dcooper said:If I have 10 #12 in a pipe or 10#14 in a pipe why do you have to derate? They only have to be fused and 20 amps and 15 amps....the wire is rated for more.
dcooper said:If I have 10 #12 in a pipe or 10#14 in a pipe why do you have to derate? They only have to be fused and 20 amps and 15 amps....the wire is rated for more.
dcooper said:I spoke with one the area code instuctors.....and #12 romex is rated for 25 amps. It must be fused @ 20. So the wire is already derated.