When is it legal to derate a neutral on a commercial 3 phase service with a 120/240 v 3 phase high leg system ?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When is it legal to derate a neutral on a commercial 3 phase service with a 120/240 v 3 phase high leg system ?
Any time you can calculate the greatest possible neutral current; typically based on the greater 120v loads on one phase.
 

dhsvcs

Member
Location
miami
Occupation
electrician
Thanx....read the section and am applying it to a job I'm working on now...( setting up the plans / as builts ) before seeing my P.E. )
 