I am looking for some input on my interpretation of 310.15(B)(4)(a).
As I understand it, this section is referring to a neutral conductor in a polyphase system that only carries unbalanced current from a "circuit" such as a 3 phase 4 wire Wye.
Examples would be a panel feeder, or a full boat (3 hot conductors of different phases, a common neutral, and hopefully an equipment grounding conductor:roll: ) serving convenience receptacles where the loads have been properly engineered.
The reason I am asking the question is that the company I work for has recently been embroiled in a debate with an engineering firm over what counts as a "current carrying conductor".
Briefly, we were forced by the Engineer and Construction Manager to abandon, and fill with concrete, all branch circuit conduits run in the underground and utilize 2" underground conduits that we believed were intended as future conduits for branch circuits (each panel has one 2" conduit that crosses an open area underground).
Their position is that in a 20 amp branch circuit, with a dedicated neutral, the neutral is not a CCC . This is allowing them to use a much lower derating factor (one of these conduits has 23 single phase circuits with dedicated neutrals) than we feel needs to be used. If they were using proper derating factors, the 2" conduits would not be sufficient and they would have to give us a change order to reroute this stuff overhead.
So, in a nutshell, what is eveyone's opinion on when it is necessary to count a neutral as a current carrying conductor?
As I understand it, this section is referring to a neutral conductor in a polyphase system that only carries unbalanced current from a "circuit" such as a 3 phase 4 wire Wye.
Examples would be a panel feeder, or a full boat (3 hot conductors of different phases, a common neutral, and hopefully an equipment grounding conductor:roll: ) serving convenience receptacles where the loads have been properly engineered.
The reason I am asking the question is that the company I work for has recently been embroiled in a debate with an engineering firm over what counts as a "current carrying conductor".
Briefly, we were forced by the Engineer and Construction Manager to abandon, and fill with concrete, all branch circuit conduits run in the underground and utilize 2" underground conduits that we believed were intended as future conduits for branch circuits (each panel has one 2" conduit that crosses an open area underground).
Their position is that in a 20 amp branch circuit, with a dedicated neutral, the neutral is not a CCC . This is allowing them to use a much lower derating factor (one of these conduits has 23 single phase circuits with dedicated neutrals) than we feel needs to be used. If they were using proper derating factors, the 2" conduits would not be sufficient and they would have to give us a change order to reroute this stuff overhead.
So, in a nutshell, what is eveyone's opinion on when it is necessary to count a neutral as a current carrying conductor?