Derating And pipe fill

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Does pipe fill , and derating rules apply to 24v systems? I'm trying to design and up coming project and can't find anything in the nec in regards to this

Sent from my SM-G965U using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Control circuits are typically Article 725 installations. 725.3(A) says that the raceway fill requirements of the xxx.22 sections of the raceway articles apply. If the control circuit conductors part of a Class 1 circuit, see 725.51(A) for ampacity adjustment. See 725.130 if the control circuits are Class 2 or 3 circuits. The rules are not clear, but the typical assumption is that ampacity adjustment is not required.
 