Did Robert mean mean 480Y/277? If so, what about the neutral? And derating for all conductors are iin the same raceway?
Phil Corso
Phil Corso
Some, yes. Enough that derating would not be necessary, who knows?
If you put a condulet every 24" without branching off, would you dissipate more heat? ...or less?
I think that the argument here is that the NEC wording does not support the practical applicaiton. In your example the conduit bodies would do little to disapate heat.
That is my point.
Well then, let's use a more practical scenario...I agree with both of you, but at same time putting a box every 2 feet really is not a violation as worded. Would also cost more than using larger conductors in most cases so the problem kind of takes care of itself.
We don't have to obey the laws of physics....only the laws of the NECWord smithing does not trump physics.:happyno: If you can lawyer up a thesis as to why your scheme "meets the letter of the code", it still may overheat.:happysad:
Word smithing does not trump physics.:happyno: If you can lawyer up a thesis as to why your scheme "meets the letter of the code", it still may overheat.:happysad:
We don't have to obey the laws of physics....only the laws of the NEC![]()