Drawing calls for eight each #12 THHN conductors to be installed in an existing 3/4" EMT home run. There are five hot conductors (ABCAB) two neutrals and a ground, (120/208 3 phase).
Counting the two neutrals as current carrying conductors, there are then 7 current carrying conductors. (Do they count or don't they? I've seen it argued both ways - what is the forum consensus?).
(2002 NEC) Table 310.15(B)(2)(a) indicates that for between 7 - 9 current carrying conductors the circuits must be derated to 70% of the allowed values in Table 310.16 through 310.19.
Table 310.16 indicates that for #12 THHN the maximum allowed ampacity is 30 Amps.
70% of 30 Amps is 21 Amps.
Footnote to Table 310.16 refers to 240.4(D) which states OCP cannot exceed 20 Amps for a #12 conductor.
The OCP required by 240.4(D) is less than the derated circuit calculation by one amp.
There is no need to take additional measures to derate the circuits in this case as the requirements of 240.4(D) accomplish the same thing.
Is this correct interpretation of the code requirement?
Counting the two neutrals as current carrying conductors, there are then 7 current carrying conductors. (Do they count or don't they? I've seen it argued both ways - what is the forum consensus?).
(2002 NEC) Table 310.15(B)(2)(a) indicates that for between 7 - 9 current carrying conductors the circuits must be derated to 70% of the allowed values in Table 310.16 through 310.19.
Table 310.16 indicates that for #12 THHN the maximum allowed ampacity is 30 Amps.
70% of 30 Amps is 21 Amps.
Footnote to Table 310.16 refers to 240.4(D) which states OCP cannot exceed 20 Amps for a #12 conductor.
The OCP required by 240.4(D) is less than the derated circuit calculation by one amp.
There is no need to take additional measures to derate the circuits in this case as the requirements of 240.4(D) accomplish the same thing.
Is this correct interpretation of the code requirement?