True.i appreciate your time but i am still confused with this because if your conduit is oversized it dissipates the heat more.
And that is your real answer.i know this is code and we have to follow it
Think about a 4 inch pipe run horizontally. All the wires will be bundled on top of each other creating heat. Sure there is more air but eventually that air will heat also.i appreciate your time but i am still confused with this because if your conduit is oversized it dissipates the heat more. i know this is code and we have to follow it
i appreciate your time but i am still confused with this because if your conduit is oversized it dissipates the heat more. i know this is code and we have to follow it
Just remember that you have to derate them, if there are more than three calculator-carrying engineers in a cubicle.. . . but I suspect that . . . the cost of getting a suitably trained engineer to do the calculations properly would exceed the cost of simply using larger wire. . . .
I agree with Jon's answer, but will add that it would be too difficult to write, let alone enforce, a rule that said we have to derate unless the conduit is this size and the conductors are that size. Imagine all the possible combinations that would have to be described in detail, and recognize that for any given combination (e.g., not more than 7 #12 conductors combined with 2 #14 conductors in a 3 inch EMT), there would have to be a engineered calculation or a lab experiment to prove that that combination could be safely installed without having to derate in that particular set of circumstances. It is simply not practical to do anything other than say, count the current-carrying conductors, and then follow this table.. . . but i am still confused with this because if your conduit is oversized it dissipates the heat more.
...The code does permit 'engineering supervision' to be used to actually calculate the ampacity of the conductors in a given situation...
...I agree with Jon's answer, ...
...True. ...
I look at this like an oven. The larger the oven the longer it might take to heat, but eventually the temperature will be obtained.
Another way to think of it is that the code rules are only simplified conservative approximations, not bleeding edge maximum performance calculations.
I have used a program called Ampcalc to obtain ampacities for underground ductbanks. It allows you to input the conduit size. But I have not done a test to see if it gives a different ampacity when you change the conduit size and make no other changes.charlie, jon, roger - I have never seen a math model, research, or paper on the heat dissipation depending on conduit size. Nehr-McGrath doesn't take conduit size into consideration.
Is the derating the same if they have slide rules instead of electronic calculators?:roll:Just remember that you have to derate them, if there are more than three calculator-carrying engineers in a cubicle.![]()
Lots heavier derate for the slie rule carriers. And there are at least two different slide rule rates that I know of. My 25cm bamboo Hemi heats up a lot quicker than my 15cm circular aluminumIs the derating the same if they have slide rules instead of electronic calculators?:roll: